will a ac vacuum pump with r134 fittings work for vacuuming my sysytem out. i have to change the fittings right. or do i need a vac for r12. going to swich to r134. also should change anything else.
will a ac vacuum pump with r134 fittings work for vacuuming my sysytem out. i have to change the fittings right. or do i need a vac for r12. going to swich to r134. also should change anything else.
The same vacuum pump will work for both R12 & R134.
The refrigerant recovery systems are not interchangeable. Do not use a recovery system for R134 with a R12 system, nor a recovery system for R12 with R134.
For a cheap alternative to a commercial vacuum pump, use an old refrigerator compressor. Mine draws 28.5" vacuum and was free!
im sorry. i guess i dont understand what a recovery system is. the pump that i am looking to buy. says comes with r-134 connectors. can i use it to vac my system thanks. sorry to be a pain.
What model is the pump & who makes it? Pumps that use compressed air for a power source are not good enough to pull the 28" of vacuum that you are going to need.
A refrigerant recovery system is used to suck out all the old refrigerant from an A/C system and put it in a recycle storage tank. It is illegal to discharge any type of refrigerant into the atmosphere.