Home electrical wiring help

  • Thread starter Thread starter 02 281 GT
  • Start date Start date May 15, 2010

02 281 GT

Agreed...My wife has great Boobs
15 Year Member
Feb 3, 2009
3,208
1,972
194
Cabot, AR
May 15, 2010
#1
  • May 15, 2010
  • #1
I've never done home wiring before, so I figured I'd see if any of y'all could help me out.

I have a 5hp Ingersoll Rand 60 gallon air compressor that runs off of 15 amps and 240 volts, however, there is no plug in the garage that can supply this power. I want to run a new plug straight off of the breaker box (which is in the garage already), and I'm just wondering if I have everything I need (and if I do, is it the right stuff).

Everything. Disregard the small gauge wire. That was for something else and kind of sneaked into this photo.
View attachment 219249

Wire.
View attachment 219250

This is the kind of plug that the power cord requires.
View attachment 219251

20 amp circuit breaker.
View attachment 219252

Spec plate on the air compressor.
View attachment 219253
 

Adam95GT

New Member
Aug 14, 2006
2,564
3
0
Burlington, NJ
May 15, 2010
#2
  • May 15, 2010
  • #2
i have no info but would like to see some... i can wire a car but my house wiring always is a fail
 

toyman

10 Year Member
Jul 19, 2007
1,944
54
79
Vernon BC
May 15, 2010
#3
  • May 15, 2010
  • #3
The wire is wrong. You need 3 wire (red, black & white) with ground and minimum 10 gauge. The circuit breaker doesn't look correct either. you need one that is usually double wide for the 240v. Red will go to one and the black to the other. The electrical box is 4x4 as the two standard 240v plug receptacles are for dryers and stoves. The plug you use on the compressor must match the blade configuration of the receptacle. If the wires from the service panel to the outlet box are going to be exposed in the garage you will also need to use specially wrapped conductor. I don't recall it's name but it's usually black and you will need the compression fittings where it connects to the box and panel and clips to hold it to the wall.
 

02 281 GT

Agreed...My wife has great Boobs
15 Year Member
Feb 3, 2009
3,208
1,972
194
Cabot, AR
May 15, 2010
#4
  • May 15, 2010
  • #4
Yeah, that's what some other people told me. I think I'm just going to call a pro on this one.
 

Adam95GT

New Member
Aug 14, 2006
2,564
3
0
Burlington, NJ
May 15, 2010
#5
  • May 15, 2010
  • #5
yea... its odd crap... i need the 240 for a powder coating oven :/
 

rd

Founding Member
Jan 12, 2000
3,316
63
109
Ocean Springs MS
May 15, 2010
#6
  • May 15, 2010
  • #6
Yes the wire needs to be two phase conductors, neutral and a ground. The receptacle by amps and configuration needs to match the plug on the compressor, or you hard wire it. But if you hard wire it, you need a disconnect means with in sight or 25 ft, iirc. Also think you need a 30 amp breaker for a 30 amp circuit.

Also need to completely shut off the panel, and lock it out, when installing the breaker.

Also consider how you are going to get the wire to the box, ie, drilling and fishing through the wall. And cut a nice hole in the wall for the box.

I do most of my home electrical, but have a staff at work who can give detailed advice, and I have a bunch of books on wiring.
 

Celeb

20+ Year Stangneter
Sep 8, 2002
736
13
59
Here and there
May 15, 2010
#7
  • May 15, 2010
  • #7
Remember to get some staples, or some other means to secure the wire after you run it.
 

02 281 GT

Agreed...My wife has great Boobs
15 Year Member
Feb 3, 2009
3,208
1,972
194
Cabot, AR
May 16, 2010
#8
  • May 16, 2010
  • #8
Routing the wire would be no problem since it's in the garage. The side on which it would be routed has no drywall. I could just set up the plug and route the wire and get the pro to hook it up to the box.
 

toyman

10 Year Member
Jul 19, 2007
1,944
54
79
Vernon BC
May 17, 2010
#9
  • May 17, 2010
  • #9
02 281 GT said:
Routing the wire would be no problem since it's in the garage. The side on which it would be routed has no drywall. I could just set up the plug and route the wire and get the pro to hook it up to the box.
Click to expand...

Having no drywall really makes the job easy. Drill holes (3/4") in the studs from the service panel to where you want the plug located. Standard 10 gauge 3 wire + ground, plug and two 30A breakers. Connecting to the service panel assuming there is extra capacity available is easy enough. Trip the main (should be marked and at the top of the panel). Take the cover off punch out two adjoining knock outs where the two circuit breakers are going. Connect the red wire to one of the breakers and the black to the other snap them into the panel and wire the white to the neutral buss and the ground to where other grounds are connected. Put the cover back on, pin the two new breakers together, reset the main breaker and you're done.
 

ProKiller

Founding Member
Apr 26, 2002
3,064
15
78
PA
May 17, 2010
#10
  • May 17, 2010
  • #10
toyman, good basic install instructions.
 

02 281 GT

Agreed...My wife has great Boobs
15 Year Member
Feb 3, 2009
3,208
1,972
194
Cabot, AR
Jul 2, 2010
#11
  • Jul 2, 2010
  • #11
I took toyman's advice and upgraded to 10-gauge wire +ground and a twin-pole 30-amp breaker. Hooked it up tonight and it worked like a charm!

Pics.
View attachment 214577
View attachment 214578
View attachment 214579
View attachment 214580
View attachment 214581
 

toyman

10 Year Member
Jul 19, 2007
1,944
54
79
Vernon BC
Jul 2, 2010
#12
  • Jul 2, 2010
  • #12
There you go. Good to hear back.
 
You must log in or register to reply here.

Similar threads

D
6G alternator pigtail wiring help needed
  • Dogman_1969
  • Aug 11, 2025
  • 1979 - 1995 (Fox, SN95.0, & 2.3L) -General/Talk-
Replies
3
Views
335
1979 - 1995 (Fox, SN95.0, & 2.3L) -General/Talk- Aug 11, 2025
Dogman_1969
D
96 GT 4.6 w/ dirty spark plug well
  • Mustang Momma
  • Apr 7, 2026
  • 1996 - 2004 SN95 Mustang -General/Talk-
Replies
3
Views
105
1996 - 2004 SN95 Mustang -General/Talk- Apr 9, 2026
LILCBRA
M
Help! 2003 GT misfire when hot
  • Modular03
  • Feb 10, 2026
  • SN95 4.6L Mustang Tech
Replies
4
Views
320
SN95 4.6L Mustang Tech Feb 13, 2026
Mustang5L5
A
88 Foxbody Starts but Stalls When Warm Please Help
  • airforcerob
  • Apr 2, 2025
  • 1979 - 1995 (Fox, SN95.0, & 2.3L) -General/Talk-
Replies
6
Views
430
1979 - 1995 (Fox, SN95.0, & 2.3L) -General/Talk- Apr 4, 2025
Noobz347
P
2000 GT Random Power Loss
  • Pinellas50
  • Mar 9, 2026
  • SN95 4.6L Mustang Tech
Replies
4
Views
246
SN95 4.6L Mustang Tech Mar 23, 2026
Pinellas50
P
Share:
Bluesky Email Share Link
  • Mustang Forums
  • 1979 - 1995 (Fox, SN95.0, & 2.3L) -General/Talk-
Menu
Log in

Register

  • Forums
  • What's new
  • Media
  • Resources
  • Contact
  • Sponsor
X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?

X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?