90

Active Member
Sep 24, 2006
0
1
43
Michigan insane asylum
Dec 1, 2006
#41
  • Dec 1, 2006
  • #41
aside from all that other stuff, if it is 10wire, its not rated for 40-60 amps.... look at my last post on page one of this thread for accurate NEC voltage for 10 wire! that came out of my uglys book i have sitting right in front of me!
 
F

fastranger347

New Member
Nov 4, 2006
59
1
0
york PA.
Dec 1, 2006
#42
  • Dec 1, 2006
  • #42
put in a new recepticle and run a new wire and install a new breaker, then you know its done right, if you cant do it, find someone who can, it will save you a lot of aggrevation from trying to figure wire guage and breaker amperage, and yes any two pole breaker will be in the 220-240 range and any single pole breaker will be in the 110-120 range, ALL depending on the pole transformer size and the load on the grid at the time of useage
 

Mustang5L5

That is…until I whipped out my Bissell
Mod Dude
Feb 18, 2001
43,236
17,922
224
Massachusetts
Dec 1, 2006
#43
  • Dec 1, 2006
  • #43
2000xp8 said:
My point is that you guys are making a very simple situation confusing for the original poster.
Click to expand...


I would agree. I would have just plugged the damn thing in and called it a day.




One has to realize the liability of coaching someone through something like this.
 

Strype

Cuthbert catcher
Founding Member
May 11, 1999
61
34
104
Huntsvegas, AL
Dec 1, 2006
#44
  • Dec 1, 2006
  • #44
@ Thread



90 is smart?
 

bynummustang

Seen my other Jackstand?
Jul 24, 2005
1
2
69
NC State University
Dec 1, 2006
#45
  • Dec 1, 2006
  • #45
I can't just plug it in, and hope it doesn't burn the place down. I know that I'll have to get a new plug because on the welder the cord has the 2 hots, and one ground, but the ground terminal looks like the ground on a extension cord, just bigger. As you can see on the original picture, the third slot isn't round, so I know I'll have to do some things just for that, but what, I'm not sure.
 

90

Active Member
Sep 24, 2006
0
1
43
Michigan insane asylum
Dec 1, 2006
#46
  • Dec 1, 2006
  • #46
im not smart im an electrician... LOL
 

Mustang5L5

That is…until I whipped out my Bissell
Mod Dude
Feb 18, 2001
43,236
17,922
224
Massachusetts
Dec 1, 2006
#47
  • Dec 1, 2006
  • #47
bynummustang said:
I can't just plug it in, and hope it doesn't burn the place down. I know that I'll have to get a new plug because on the welder the cord has the 2 hots, and one ground, but the ground terminal looks like the ground on a extension cord, just bigger. As you can see on the original picture, the third slot isn't round, so I know I'll have to do some things just for that, but what, I'm not sure.
Click to expand...


So the receptacle needs to be changed.

If you don't know what you are doing, you really should call an electrician. Explaining how to do that is pretty complex and a huge liability for the guys that are liscensed. If you burn your home down we could be responsible.


BTW, i am also a liscensed electrician...although i work as an engineer...go figure.
 

90

Active Member
Sep 24, 2006
0
1
43
Michigan insane asylum
Dec 1, 2006
#48
  • Dec 1, 2006
  • #48
if he figure out how to shut that recptical off ill take the liablity through PM's and walk him threw it! with detailed pic's!
 
F

fastranger347

New Member
Nov 4, 2006
59
1
0
york PA.
Dec 2, 2006
#49
  • Dec 2, 2006
  • #49
he needs to post a picture of the plug thats on the welder, the way he describes the plug, i picture it as a 120v-30amp rv style plug
 

2000xp8

SN Certified Technician
Aug 8, 2003
8,023
1,615
194
NJ
Dec 2, 2006
#50
  • Dec 2, 2006
  • #50
Mustang5L5 said:
.

If you don't know what you are doing, you really should call an electrician. Explaining how to do that is pretty complex and a huge liability for the guys that are liscensed. If you burn your home down we could be responsible.


BTW, i am also a liscensed electrician...although i work as an engineer...go figure.
Click to expand...

Agreed, if i this thread has gone this far and he hasn't figured it out, he should call someone to come and do it.
If it's just a simple breaker and outlet change, i'd probably charge him like $125.
 

bynummustang

Seen my other Jackstand?
Jul 24, 2005
1
2
69
NC State University
Dec 2, 2006
#51
  • Dec 2, 2006
  • #51
All the pics of the stuff i have

here are all the pics:





















So am I in for an electrician?
 

Attachments

  • PB290118.webp
    30.7 KB · Views: 78
  • PB290119-1.webp
    48.4 KB · Views: 72
  • PB290120.webp
    40.1 KB · Views: 83
  • PB290121.webp
    16.4 KB · Views: 82
  • PB290122.webp
    32.9 KB · Views: 84
  • PC010123.webp
    29.5 KB · Views: 73

5.0Droptop

...all those nights we shared, and you're a dude??
Special Agent Mukity-Muck Whats in Charge Round Here
May 15, 2002
1,785
1,130
233
Indiana
Dec 2, 2006
#52
  • Dec 2, 2006
  • #52
I sent the pics you wanted Bynumstang.

Change the outlet socket and it should be a go as long as the wiring is up to par.
Listen to 2000xp8.... Joe knows his stuff.
 

Mustang5L5

That is…until I whipped out my Bissell
Mod Dude
Feb 18, 2001
43,236
17,922
224
Massachusetts
Dec 2, 2006
#53
  • Dec 2, 2006
  • #53
Damn, it's 50A input. That kinda changes things.

What you have now is a 20A 230V single phase receptacle...what you NEED for that welder is a 50A 230V single phase receptacle.

Unfortunately to run that will require a 50A 2-pole breaker, a 50A 250V 2-pole, 3-wire receptacle and #6 wiring. I'm not 100% sure on the wire size though since it's 230V, you may be able to use #10. Table 210.25 in the NEC specs #6 for 50A branch circuits.

Also, i see four 2-pole breakers in your panel. Do you know what the amp ratings are on those breakers?? I bet you your receptacle is currently running off a 20A breaker.


Wait for one of the other guys to confirm what i said first. My electrical expierence is mostly controls such as bridges. Not really a "plug and switch" guy
 

sweet88gt

Member
Jun 25, 2005
334
0
16
Venice FL
Dec 3, 2006
#54
  • Dec 3, 2006
  • #54
The wire you have a close up picture for is 12-2. Its only rated for 20 amps. You will need a dedicated circuit for that welder. It needs to be a 2 pole 50 amp breaker with #6 wire. If that picture shows the main panel another thought may be what is the amperage rating for the MAIN breaker in that panel?? The wiring for the outlet you have is not going to work. In your case an electrican is probably in your future. On a side note,that seems to be a nice welder.
 

bynummustang

Seen my other Jackstand?
Jul 24, 2005
1
2
69
NC State University
Dec 3, 2006
#55
  • Dec 3, 2006
  • #55
Hmm, I think what I will end up doing is selling the welder. I payed not that much, but it will cost much more than the welder to get it pluged up and ready. I might as well just get something that will run off 110.

Crap, well time to go take pictures and clean it up, and set it up on craigslist.
 

Mustang5L5

That is…until I whipped out my Bissell
Mod Dude
Feb 18, 2001
43,236
17,922
224
Massachusetts
Dec 3, 2006
#56
  • Dec 3, 2006
  • #56
If you can find a 230V 20A input welder you are good to go.

50A is a lot of juice. That might be half your load for your household panel if that's a 100A older service
 

bynummustang

Seen my other Jackstand?
Jul 24, 2005
1
2
69
NC State University
Dec 3, 2006
#57
  • Dec 3, 2006
  • #57
Yeah, I'll see if I can turn my money back on this welder.
 

90

Active Member
Sep 24, 2006
0
1
43
Michigan insane asylum
Dec 3, 2006
#58
  • Dec 3, 2006
  • #58
that wire looks like 12-2... and if you look on page 1 i called that out of the blue! i said 14-2 was white, but the older stuff 12 wire was white... so i think your screw'd...
but i gotta run!, ill help you out just not right now!
 

2000xp8

SN Certified Technician
Aug 8, 2003
8,023
1,615
194
NJ
Dec 3, 2006
#59
  • Dec 3, 2006
  • #59
50amp welder for the home is a bit on the extreme side. If your panel is in the garage it's still pretty simple to hook up, but may be too much of a power hog.
And from the looks of it, your house has electric appliances which is not good if you are adding more.
4 220v breakers means you are probably already drawing alot of juice.
 
F

fastranger347

New Member
Nov 4, 2006
59
1
0
york PA.
Dec 3, 2006
#60
  • Dec 3, 2006
  • #60
how much you want for it
 
Prev
  • 1
  • 2
  • 3
  • 4
Next
First Prev 3 of 4 Next Last
You must log in or register to reply here.

Similar threads

E
2007 GT Stalls when lights or a/c turned on
  • ejscarfo
  • Jun 22, 2026
  • 2005 - 2009 Specific Tech
Replies
2
Views
115
2005 - 2009 Specific Tech Jun 29, 2026
ejscarfo
E
Fuel Anyone know a part number for a 3/8" inlet/outlet efi quick connect fuel filter that would fit the stock foxbody location?
  • rednotch
  • Dec 8, 2025
  • Fox 5.0 Mustang Tech
Replies
2
Views
274
Fox 5.0 Mustang Tech Dec 8, 2025
rednotch
F
2004 Mustang GT – Fuel Pump Not Priming
  • Fayio
  • Apr 22, 2026
  • SN95 4.6L Mustang Tech
Replies
7
Views
255
SN95 4.6L Mustang Tech Apr 27, 2026
n0v8or
N
8
Did I fry something messing with my ignition?
  • 85gtCOBRA
  • Oct 18, 2025
  • 1979 - 1995 (Fox, SN95.0, & 2.3L) -General/Talk-
  • 2
Replies
30
Views
1K
1979 - 1995 (Fox, SN95.0, & 2.3L) -General/Talk- Nov 15, 2025
85gtCOBRA
8
Pro-M 75MM Bullet Flow Sheet - Is this calibrated for 36 # injectors?
  • dan50
  • Jan 11, 2026
  • Digital Self-tuning Forum
Replies
2
Views
306
Digital Self-tuning Forum Jan 11, 2026
dan50
Share:
Bluesky Email Share Link
  • Mustang Forums
  • 1979 - 1995 (Fox, SN95.0, & 2.3L) -General/Talk-
Menu
Log in

Register

  • Forums
  • What's new
  • Media
  • Resources
  • Contact
  • Sponsor
X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?

X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?