witch braided hose for mecanical fuel pressure gauge?

  • Thread starter Thread starter bock
  • Start date Start date May 14, 2004

bock

Founding Member
Jan 7, 2002
648
2
19
Montreal,Qc
May 14, 2004
#1
  • May 14, 2004
  • #1
For now, i have a 1 inch fuel pressure gauge on the fuel line.I want to move it away for the headers,is case of failure and fire.I just want to fix it on the firewall ,in the corner under the hood.

Can i use braided stainless steel brake line rated at 2500 psi for this?
 
P

proxses

Founding Member
Dec 12, 2000
620
0
0
Dayton, Oh
May 14, 2004
#2
  • May 14, 2004
  • #2
I would check to see what material the line is made of. It needs to be able to resist the additives they now put in gasoline.
But most likely it should be ok as long as you can adapt the fittings.
Oh, also, the line may be a bit small as far as the inside diameter is concerned. You may not get proper flow. Most brakes are about a -3AN size, while they have fuel pressure gauges run a -4AN. Not too much of a difference.
Anyway, if it is teflon lined, your ok. I would just test it to see if your readings seem accurate, because of the smaller line, after the change.
 

powershift351

New Member
Apr 2, 2004
225
0
0
Carlsbad, Ca.
May 14, 2004
#3
  • May 14, 2004
  • #3
aeromotive
 

hllon4whls

BANNED
Founding Member
Jan 17, 2002
2,567
0
46
Covington
May 14, 2004
#4
  • May 14, 2004
  • #4
You dont need flow to a fuel pressure gauge. You just need enough diameter to assure the proper pressure. I would suspect that the brake line would not be affected by the gasoline, but I personally have never tried it.
 
J

Jayber

New Member
May 9, 2004
32
0
0
May 14, 2004
#5
  • May 14, 2004
  • #5
Brake fluid is way more corrosive than gasoline. Brake line will work fine.
 

bock

Founding Member
Jan 7, 2002
648
2
19
Montreal,Qc
May 16, 2004
#6
  • May 16, 2004
  • #6
Im gonna try it.
 

bock

Founding Member
Jan 7, 2002
648
2
19
Montreal,Qc
May 16, 2004
#7
  • May 16, 2004
  • #7
what s ya think?
 

89MustangGX

I have nothing productive to add!
Jul 3, 2001
10,262
1
0
Mill Creek, WA
May 17, 2004
#8
  • May 17, 2004
  • #8
Only thing that concerns me is having the gauge on the firewall. I might want to either put it above (like on the cowl) or on one of the fenders. That way if a fitting breaks or loosens up you don't have pressurised fuel spraying at the firewall.
 

HISSIN50

"How long does it take to get help in here?
15 Year Member
Nov 29, 1999
31,179
34
129
May 17, 2004
#9
  • May 17, 2004
  • #9
i checked in cuz im curious about this (gonna do it soon)...doesnt Jegs, etc sell the correct line and fittings?
sorry if i missed something and am totally wrong...good luck.
 

jrichker

StangNet's favorite TOOL
In Remembrance. Thank you for your contributions
Mar 10, 2000
27,512
2,813
234
Dublin GA
May 17, 2004
#10
  • May 17, 2004
  • #10
Put a flow limiter in any gauge line you are concerned about breaking. As Hllon4whls has said, flow isn't a concern when all you are doing is reading pressure. A flow restrictor can be as simple as tapping the inside of the fitting nearest the pressure source to a common size like a 10-32 machine screw thread. Then drill a short matching thread machine screw with a 1/16" or smaller drill all the way down from the head to the other end. Coat the threads with blue silicone sealer and screw it in. Then cut off the part that stick out and assemble the rest of the fittings. Then if the line breaks, there will be a much smaller volume of liquid squirting out all over the place.

You can buy the Autometer Stainless Steel braided hose for like $60. Or a local shop that makes hydraulic hose assemblies can make it for you at a cheaper price. Ordinary low pressure hydraulic hose can be used in place of the Stainless Steel braided hose, the Stainless Steel braided hose just looks nice. I got mine for $4 at a place that sells industrial and military surplus parts of all kinds. The Stainless Steel braided hose goes for about $3.60 a foot and the fittings are probably about $5-$8 each. You can make your own and save some $$$, the shops may have a setup or labor charge to fabricate the hose assembly.
 

bock

Founding Member
Jan 7, 2002
648
2
19
Montreal,Qc
May 17, 2004
#11
  • May 17, 2004
  • #11
I already have a 3 feet brake hose, that why im asking!
 

jrichker

StangNet's favorite TOOL
In Remembrance. Thank you for your contributions
Mar 10, 2000
27,512
2,813
234
Dublin GA
May 17, 2004
#12
  • May 17, 2004
  • #12
bock said:
I already have a 3 feet brake hose, that why im asking!
Click to expand...

Teflon lined hose is Ok. Non-teflon brake hose is not likely compatible with petrolem based fluids like oil & gasoline.
 

bock

Founding Member
Jan 7, 2002
648
2
19
Montreal,Qc
May 17, 2004
#13
  • May 17, 2004
  • #13
brake oil,is not petrolem based fluid?
 

bock

Founding Member
Jan 7, 2002
648
2
19
Montreal,Qc
May 19, 2004
#14
  • May 19, 2004
  • #14
ok, i saw on the Allstar performance site,that its a teflon hose,so i should be ok.
 
You must log in or register to reply here.

Similar threads

M
01 mustang 3.8 fuel pressure issue
  • Mhaley2006
  • May 29, 2026
  • 1996 - 2004 SN95 Mustang -General/Talk-
Replies
0
Views
169
1996 - 2004 SN95 Mustang -General/Talk- May 29, 2026
Mhaley2006
M
B
'03 GT Fuel Pump/Pressure/Delivery Issue
  • Brodach
  • Oct 21, 2025
  • SN95 4.6L Mustang Tech
Replies
8
Views
924
SN95 4.6L Mustang Tech Oct 31, 2025
gkomo
SURGING IDLE / NO IDLE CHECKLIST FOR 1996–1998 MUSTANG GT (4.6L 2V) - Work In Progress
  • Noobz347
  • Aug 30, 2025
  • 1996 - 2004 SN95 Mustang -General/Talk-
Replies
0
Views
753
1996 - 2004 SN95 Mustang -General/Talk- Aug 30, 2025
Noobz347
SURGING IDLE / NO IDLE CHECKLIST FOR 1999–2004 MUSTANG GT (4.6L 2V) - Work In Progress
  • Noobz347
  • Aug 30, 2025
  • 1996 - 2004 SN95 Mustang -General/Talk-
Replies
0
Views
934
1996 - 2004 SN95 Mustang -General/Talk- Aug 30, 2025
Noobz347
SN95 The Unicorn
  • HANO Motorsports
  • May 18, 2025
  • 1979 - 1995 (Fox, SN95.0, & 2.3L) -General/Talk-
  • 2
Replies
21
Views
1K
1979 - 1995 (Fox, SN95.0, & 2.3L) -General/Talk- Aug 15, 2025
HANO Motorsports
Share:
Bluesky Email Share Link
  • Mustang Forums
  • 1979 - 1995 (Fox, SN95.0, & 2.3L) -General/Talk-
  • Fox 5.0 Mustang Tech
Menu
Log in

Register

  • Forums
  • What's new
  • Media
  • Resources
  • Contact
  • Sponsor
X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?

X

Privacy & Transparency

We use cookies and similar technologies for the following purposes:

  • Personalized ads and content
  • Content measurement and audience insights

Do you accept cookies and these technologies?